Advice on water pressure and pressure relief valve

Joined
9 Mar 2026
Messages
37
Reaction score
5
Country
United Kingdom
Hi there
I recently replaced my kitchen tap and turned off the water using the stop cock under the kitchen sink when doing so. There is a pressure gauge next to the stop cock and I believe it is next to a Pressure Relief Valve. Before I started the job it looks like the pressure reading is abot 4.5 but there is a red/orange needle pointing at 3.

I read that having the pressure too high can cause pipe banging which is something we experience regularly - mainly when the washing machine is on.

I therefore (with my lack of plumbing knowledge) thought I should reduce the pressure a bit to prevent this banging so I didn't completely open the stock cock (so I think). My hot tap in the utility room is coming out cloudy (air bubbles I believe as it clears in a glass from the bottom upwards). I am pretty sure this didn't happen prior to me replacing the main kitchen tap. I therefore am wondering if the settings for the stop cock is causing this. I did read that the stop cock should be fully opened. I tried turning it anticlockwise more to open it last night but it just keeps turning and it actually leaked a small pool of water out (about a couple of tablespoons max). I turned it clockwise again a bit for fear this could become more than an small pool. I left it all night and there was no additional water.

So I have a couple of questions. One is can I safely keep turning the stop cock tap handle anticlockwise and will it eventually stop. My fear was it would just pop off and I would get loads of water. I did read that it should have a hard stop at some point.

The other question relates to the red/orange needle pointing at 3 on the pressure gauge. I am assuming this is recommending a max of 3 bars. When I initially turned the stop cock back on after my tap replacement I only partially undid it and pressure was sitting around 3 but the water pressure for the cold water was very weak upstairs. Note I have a worcester greenline boiler and a hot tank in the airing cupboard upstairs (I believe it is gravity fed but could be wrong). There is no cold water or any tank in the attic.

So should I be turning the Pressure Relieve Valve at all. Note I have never touched this before but looks like you can turn the blue bit at the bottom.

Note the tap photo is the tap that is delivering the cloudy hot water. Also note the hot water in the downstairs toilet is not appearing cloudy. This is a different type of tap (a mixer tap)

Any advice much appreciated.

IMG_0921.JPEG
IMG_1569.JPEG
IMG_1570.JPEG
IMG_1036.PNG
 
To be clear turning down your stop tap has zero effect on pressure it just reduces volume.
Stop tap fully open then quarter turn back to prevent sticking open.
The valve with gauge is a pressure reducing valve, it's the black needle reading pressure.
If you have no cold water cistern chances are it's a pressurised cylinder. Clear pictures of cylinder would help to confirm.
Some taps do give the clouded water effect.
When water is being used say running a bath what pressure does gauge read?
 
Thank you for the reply.
Here are some photos including the gauge reading when the hot and cold taps are turned to run a bath.
When I checked the stop cock this lunch time there was about a tea spoon of water below it.

IMG_1577.JPEG
IMG_1576.JPEG

IMG_1579.JPEG
 
yeah 4.5 bar is pretty high for domestic incoming mains mate, 3 bar is usually the sweet spot. you can adjust the screw on the prv counter-clockwise to bring it down to 3 and that should help with the pipe hammer. washing machine solenoid valves slam shut instantly which causes the banging, so if it still does it pop a tenner mini shock arrestor right on the cold feed valve behind the washer.
 
yeah 4.5 bar is pretty high for domestic incoming mains mate, 3 bar is usually the sweet spot. you can adjust the screw on the prv counter-clockwise to bring it down to 3 and that should help with the pipe hammer. washing machine solenoid valves slam shut instantly which causes the banging, so if it still does it pop a tenner mini shock arrestor right on the cold feed valve behind the washer.
I tried twisting the blue end of the PRV counter-clockwise but it doesn't appear to change the pressure at all. It is turning but it is not affecting the pressure.
 
I tried twisting the blue end of the PRV counter-clockwise but it doesn't appear to change the pressure at all. It is turning but it is not affecting the pressure.
Is that with the taps running? The pressure won't reduce until it's relieved by the flow. Turning the knob with the taps shut won't change the indication since that's residual pressure in the pipes. Try adjusting it with taps running.
 
I tried twisting the blue end of the PRV counter-clockwise but it doesn't appear to change the pressure at all. It is turning but it is not affecting the pressure.
what spherehopper said is spot on mate, if all your taps are closed you're just measuring trapped static pressure in the pipes so turning the dial won't move the gauge. crack a cold tap downstairs half open so water's flowing through it, then adjust the dial counter-clockwise and watch the needle drop. if it still won't budge even with water flowing, the internal spring or cartridge is probably scaled up and stuck.
 
what spherehopper said is spot on mate, if all your taps are closed you're just measuring trapped static pressure in the pipes so turning the dial won't move the gauge. crack a cold tap downstairs half open so water's flowing through it, then adjust the dial counter-clockwise and watch the needle drop. if it still won't budge even with water flowing, the internal spring or cartridge is probably scaled up and stuck.
Thanks for the advice. I turned on the hot and cold water taps and obviously the pressure on the gauge then reduced. I then turned the blue end of the PRV counter-clockwise about 5 or more turns but it didn't make any difference and when I turned off the taps again it returned to where it was previously on the gauge. You mention the possibility of it being scaled up and stuck. Is that a plumber job or something I could investigate myself? One thing to mention. There is a screw at the bottom of the blue cap in the centre of the cap. Even though the blue cap is turning, I wonder if I needed to turn that screw or not. I also read that sometimes you need to pull the cap downwards.
 
Last edited:
I tried twisting the blue end of the PRV counter-clockwise but it doesn't appear to change the pressure at all. It is turning but it is not affecting the pressure.
no worries mate. yeah if you've given it 5 turns and the standing pressure still creeps right back up when taps are off, the cartridge seat is either badly scaled or the diaphragm's shot letting mains pressure through. you can try unscrewing the cartridge top to descale/clean the mesh if you isolate the main stopcock first, but honestly 9 times out of 10 once they stick it's quicker and cheaper to just swap the whole valve or cartridge. pretty straightforward diy job if you're comfortable turning water off and using grips, but if the nuts are seized on the pipework get a local plumber in to save cracking a joint.
 