    Hello knowledgeable folks!

    We have a re-occuring issue with one of the radiators on our system. The rad in question is at the top of the house (rads on three levels) and is a towel rail. There is another rad on the same level, which we do not experience any issues with at all.

    We repeatedly get an airlock somewhere leading to the towel rail (feed pipe remains cold) which I can successfully resolve in the usual manner (isolate feed and return valves, remove bleed point, attach hose, open flow/return until airlock clears, replace bleed point, re-pressurise system etc) however, this is a "faff" which I am having to repeat on a regular basis.

    Three questions:

    1) Anyone know what would repeatedly cause this to happen?

    2) Anyone know how to solve it permanently

    3) Would installing an autovent (like an Aladdin) on the bleed point help to stop this happening?


    Thanks in advance (y)
     
  2. Madrab

    Madrab

    Joined:
    4 Oct 2012
    Messages:
    7,921
    Thanks Received:
    2,235
    Location:
    East Renfrewshire
    Country:
    United Kingdom
    I don't understand why you are removing the bleed point, attaching a hose and then open valves until air lock clears. Are you using the hose to force mains pressure down through the rad to clear the air lock?

    If you are constantly getting an air lock then there must be air entering the system or gas being created in the system. Are you having to top the pressure up regularly?
     
  3. Sponsored Links
  4. mjt81

    mjt81

    Joined:
    15 Mar 2013
    Messages:
    15
    Thanks Received:
    0
    Location:
    Oldbury
    Country:
    United Kingdom
    Sorry, maybe I should have added this to my original post. The hose is attached to a 1/2" adapter which I screw into the bleed point before I open the valves again and is used simply to allow water to drain out of the rad and down the loo rather than onto the bathroom floor.

    Simply opening the bleed point has no effect as water comes out immediately, so to clear the airlock, (which is somewhere on the pipes before the rad as the feed pipe doesnt get hot) I'm removing the bleed point then allowing a greater volume of water/any trapped air to flow out at a decent pressure to clear the airlock.

    Pressure seems fine. Hovers around the 1.5bar when cold. Only time I need to top it up is after I've let a load of water out following the above process.

    If there is an easier way, I'm all ears....
     
  5. jackthom

    jackthom

    Joined:
    14 Feb 2007
    Messages:
    1,342
    Thanks Received:
    236
    Location:
    Northumberland
    Country:
    United Kingdom
    How long does this radiator work properly after being bled?
     
  6. Sponsored Links
  7. mjt81

    mjt81

    Joined:
    15 Mar 2013
    Messages:
    15
    Thanks Received:
    0
    Location:
    Oldbury
    Country:
    United Kingdom
    3-4 weeks
     
  8. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page