Alpha cb24 turns of after 30 mins when c/h is turned on

Joined
19 Nov 2007
Messages
6
Reaction score
0
Location
Wolverhampton
Country
United Kingdom
I have a Alpha CB24 boiler, that works fine for about 30 minutes when central heating is turned on, then turns itself of for about 15 minutes then comes on again for about 5 minutes. The h/w out of the hot water tap is boiling hot and you can not put your hands in the hot water. you can here a hissing sound from the boiler when you turn on the central heating. I have repressured the system 2 times in a week, and both times there was a lot of air in the radiators in the upstairs bed rooms. When the central heating is turned of the h/w from the taps is fine.
 
Sponsored Links
Sounds like it is overheating, shutting off, cooling down, then coming back on.

Check the stat ntc.

If it is doing it only on ch, could be the plate HE blocked.
 