Hi all
I'm a heating engineer and was called to a faulty boiler yesterday. On investigation found that the PCB had a few burnt components and the PCB transformer was burnt out! Fair enough, a new PCB and transformer it is then. However, looking further for a cause (this boiler is still under a year old by the way) I found with the fused spur to the boiler system off I had no voltage on the live but about 150v on the neutral. I told him he had a system electrical problem, and to get it repaired before I fit he new PCB etc. I phoned the guy up today and he had a right go at me saying he's had a qualified electrician around and no problem was found...wasted money...blah...blah. So guy's am I missing something? I always thought max allowable between Earth and Neutral was about 5V?
I'm a heating engineer and was called to a faulty boiler yesterday. On investigation found that the PCB had a few burnt components and the PCB transformer was burnt out! Fair enough, a new PCB and transformer it is then. However, looking further for a cause (this boiler is still under a year old by the way) I found with the fused spur to the boiler system off I had no voltage on the live but about 150v on the neutral. I told him he had a system electrical problem, and to get it repaired before I fit he new PCB etc. I phoned the guy up today and he had a right go at me saying he's had a qualified electrician around and no problem was found...wasted money...blah...blah. So guy's am I missing something? I always thought max allowable between Earth and Neutral was about 5V?