- Joined
- 27 Jan 2008
- Messages
- 28,960
- Reaction score
- 3,545
- Location
- Llanfair Caereinion, Nr Welshpool
- Country
The resistance needs to be in the main less than an ohm, we should use a special low ohm ohmmeter to measure it, but with an ohmmeter which is part of a multi-meter looking at near zero ohms, but the exact reading will not be acerate enough to matter, so just looking for continuity.
We with a 32 amp MCB should be looking at a line - earth reading of 1.38Ω, and line to neutral more like 1Ω, measured with a loop impedance meter, but the 1.38Ω is not so important if you have RCD protection, and the 1Ω reading is really down to volt drop, but even if over the 5% allowed, it is not likely to cause a problem.
The socket tester
is designed for a radial circuit, and the pass level is too high for a ring final, and we jump from £32.50 to over £80 to get a tester that will do a ring final. But you're not running close to the limit, so not really something to worry about.
The socket tester