Planning a new kitchen install and will be looking to wire in new 7kW Induction Hob & 2 x 3kW Ovens
The ovens will be fed off their own Radial circuit, which I plan to run a 4mm Cable (~ 10m run max) to 2 x 20A Grid switches for each oven. - I will run 2.5mm to each oven from their respective switch. This Circuit will be protected by a 32A Breaker.
The Hob will again be on its own radial circuit and am thinking a 4mm cable and 32A protection will be sufficient based on;
7000W / 230V = 30A
But when considering diversity....
10A + 30% of 30A + 5A (for socket) = 24.1A
So, this is all good right?
Where I am not to sure of though is that I would like to run this cable in a metal conduit under the floor, which I think I'm right in saying is a no go for as per the regs (I may be wrong here). But in order to protect the cable against mice & possibly rats....don't ask! I want to run about 3m of the cable in conduit.
How would this effect my design? Should I step up to 6mm to account for this. And do you have any good suggestions for protecting T&E against Mice & Rats?
Cheers
The ovens will be fed off their own Radial circuit, which I plan to run a 4mm Cable (~ 10m run max) to 2 x 20A Grid switches for each oven. - I will run 2.5mm to each oven from their respective switch. This Circuit will be protected by a 32A Breaker.
The Hob will again be on its own radial circuit and am thinking a 4mm cable and 32A protection will be sufficient based on;
7000W / 230V = 30A
But when considering diversity....
10A + 30% of 30A + 5A (for socket) = 24.1A
So, this is all good right?
Where I am not to sure of though is that I would like to run this cable in a metal conduit under the floor, which I think I'm right in saying is a no go for as per the regs (I may be wrong here). But in order to protect the cable against mice & possibly rats....don't ask! I want to run about 3m of the cable in conduit.
How would this effect my design? Should I step up to 6mm to account for this. And do you have any good suggestions for protecting T&E against Mice & Rats?
Cheers