Ariston 27 Combi Boiler not working

Joined
14 Apr 2012
Messages
3
Reaction score
0
Location
London
Country
United Kingdom
The low water level led is illuminated. I have topped up the water pressure to nearly 2 bar and switching off the boiler and then on again still does not work.

Presumably a switch is preventing the water pressure being registered, if so can I over-ride it to at least get the boiler working temporarily until after the weekend?
 
The re-set button is only for ignition or over-heating shutdown. Thanks anyway.
 
If the boiler is well sludged up then the LP switch can take hours to respond to the increased water pressure.

Obviously the answer is to check the boiler pressure regularly and toping it up when required!

Tony
 
The boiler is now fixed. The pump was very stiff which has now been freed up. I guess I will have to change it eventually.

Thank you both for your reples.
 