ASHP 22mm Pipe directly to std new radiator without stepping down to 15mm

Joined
23 Nov 2026
Messages
7
Reaction score
0
Country
United Kingdom
I have an ASHP. All main pipe rums are 22mm, all radiators are oversized, standard and new.

The position of the radiators in relation to the pump means that the nearest rads in bedrooms upstairs are fed first and these rooms are overheating (For Me) i prefer a cooler bedroom. The rads furthest away are in the kitchen and living room. The system is struggling to warm up these two rooms.

If i turn down the temperature using the TRV's in the bedrooms the system complains and switches itself off (Too low water flow).

I'm thinking it may improve things if i can connect up the Kitchen and Living room radiators without stepping down the pipe size from 22mm to 15mm before connecting to the radiators.

Is this a worthwhile idea, and if it is can you get valves that allow the direct connection of 22mm pipes to std modern radiators. Would it improve water flow to these two radiators sufficiently so that i can turn down the rads in the bedrooms so that i can get a good nights sleep and have a warmer living room?

Or would it be a better idea to add another radiator to the living room? When the system was installed, the installer said that when i get the conservatory roof changed to an insulated roof (Done) the system will cope with an added radiator in the conservatory when i'm ready but instead would it be better to add another radiator to the living room to increase flow, increase warmth to that room and turn down rads in bedrooms?
 
Last edited:
Have you tried opening the lockshield valves on the kitchen and living room rads slightly?
 
Fully open.

I've tried balancing up the rads by slightly closing up the lockshield valves in the bedrooms already and it does work. But after a few hours i get the error message (Too low water Flow). Opening up the lockshield valves in the bedrooms resolves the problem but i then have bedrooms that are toooooooo warm and a living room that's not quite warm enough.

Balancing works very well for a few hours, turning the TRV's down also works but only for a few hours before the system switches off with the message that the water flow is to low.

So how can i increase water flow at the further most point in the heating system so that the system doesn't switch off?

When the system is balanced up in a way that water flow is acceptable i can have 24 degrees in the bedrooms but just 19 degrees in the living room. I'd like to try and turn this around the other way, although 20/21 will be warm enough for me in the living room.

Water from the pump travels past the bedroom radiators first on it's journey to the last radiators in the system which is the living room and the kitchen.

So naively i'm exploring if it's possible to and how to increase flow where it's needed in the Kitchen and Living Room so that i can reduce flow where i don't want it, in the bedrooms.
 
Last edited:
Sounds like you want a two-branch system with one branch feeding the upstairs rads only, the other branch feeding the downstairs rads only, and a control valve or two to apportion the flow among the two branches?
 
Could be a blockage somewhere? Or maybe this message is bogus.
Error only occurs when i reduce flow to the 5 radiators upstairs in an attempt to move more water to the two radiators downstairs. Is this essentially creating a blockage and therefore low flow!?

My message is not Bogus at all!!??

Sounds like you want a two-branch system
5 rads on the upstairs branch and just two only on the downstairs branch. I'm thinking that i'd still end up with Low water flow on the downstairs branch when flow to the upstairs branch is restricted to lower the temp upstairs.

I may be wrong but it's worth thinking about though.
 
Last edited:
I'm thinking that i'd still end up with Low water flow on the downstairs branch when flow to the upstairs branch is restricted to lower the temp upstairs.
Not if the flow could be partially diverted from the upstairs branch to go through the downstairs branch instead. The total flow should be the same. Perhaps a controlled bypass for the downstairs branch would need to be added.
 
Error only occurs when i reduce flow to the 5 radiators upstairs in an attempt to move more water to the two radiators downstairs. Is this essentially creating a blockage and therefore low flow!?

No that’s not creating a blockage. I’m suggesting that there is a physical blockage in the pipework somewhere. To me it seems improbable that with the lockshields (and TRVs?) fully open, the flow could be so restricted by the pipework that the heat pump would complain. Unless the pipes are extraordinarily long. So maybe there is a partial blockage in a pipe somewhere. Or maybe the lockshields and TRVs actually aren’t fully open?

My message is not Bogus at all!!??

The “too low flow” message that the pump is showing. I’m suggesting that maybe its flow sensor is wrong.
 
Your first port of call is your installer.
The system is not working to your satisfaction and is (hopefully) still under warrantee.

How is your system controlled and do you have a thermostat in the same room as a radiator with a TRV?
 
A thank you to those that have posted replies. I'm also exploring the idea of reversing the flow so that hot water passes the two radiators downstairs first and returning via the upstairs rads.

To me it seems improbable that with the lockshields (and TRVs?) fully open, the flow could be so restricted by the pipework that the heat pump would complain.
The system doesn't complain when the lockshields and TVR's are fully open, i'm the one complaining because i can't sleep in a bedroom that's too warm at sometimes as high as 22 degrees plus when the temp downstairs is 18 overnight. I can sleep in a bedroom at 18 and below but 18 in a living room on an evening is a tad on the cool side for me.

Trying to turn around the situation. Cooler bedrooms, warmer living room.

How is your system controlled and do you have a thermostat in the same room as a radiator with a TRV?
Roomstat in the living room where the rad has a TVR. The rad in the kitchen doesn't have a TVR. The roomstat is my only control, i could/can if i wanted to control flow temperature turn on or off weather compensation and balance rads and or turn TVR's up and down.
 
Last edited:
From point of entry into the house the pipework travels 18mtrs to get to the Kitchen radiator. It travels by 5 upstairs rads before travelling downstairs to a junction at 12mtrs from entry where it splits, 3mtrs further to the living room rad in one direction and 6mtrs to the Kitchen rad in another direction.
 
The system doesn't complain when the lockshields and TVR's are fully open

I meant, the lockshields and TRVs on the kitchen and living room radiators (only) are fully open.

From point of entry into the house the pipework travels 18mtrs to get to the Kitchen radiator. It travels by 5 upstairs rads before travelling downstairs to a junction at 12mtrs from entry where it splits, 3mtrs further to the living room rad in one direction and 6mtrs to the Kitchen rad in another direction.

That is quite a lot of pipe, more than I have experience with I guess.

As above, what do the installers say?
 
I meant, the lockshields and TRVs on the kitchen and living room radiators (only) are fully open.

Lockshield and TVR fully open on Living Room rad, their is no lockshield or TVR on the kitchen rad.

18mtrs from where the pipework enters the house to the further most rad in the kitchen can't be a lot of pipework surely?

As above, what do the installers say?

Sorry i should have answered this one already, warranty has expired and they want nothing more to do with it. The local chap who i have used to service the system just wants to rip it all out and fit a new system. Not offering any other advice at all, just doesn't want to know.
 
Running 22mm right up to the living room and kitchen valves won't change much. The 15mm tails are short, most of the resistance is in the valves and the long run, and on a normal two-pipe system the order of the radiators doesn't decide which one gets the water. So reversing the direction won't fix it either.

The clue is that it works for a few hours and then trips. As the bedrooms warm up their TRVs close a bit more, and with the lockshields already part closed the total water flow drops below what the heat pump needs. Three things to try:

- Clean the filter on the heat pump return (magnetic filter or strainer). Like endecotp said, a partial blockage would explain it, and a part-blocked filter is the usual one: fine with every valve open, trips as soon as anything closes.
- If the heat pump has a pump speed setting (or an external pump), go one step up. That keeps enough water moving with the bedrooms throttled.
- Turn the bedroom TRVs to max and set the bedrooms with the lockshields only. Then the water flow stays the same all night instead of shrinking as the TRVs close.

Then balance: measure flow and return temperature on each radiator with an IR thermometer on a strip of masking tape (bare copper gives false readings). The bedroom radiators will show a small drop between flow and return, so close those lockshields a little, wait at least 20 minutes and measure again. On a cold day about 5 °C is a rough starting point, but the aim is every room at the temperature you want with the living room valve fully open, not the same number on every radiator. It takes a few evenings.

If the living room still stops at 19 with its valve fully open and the low flow error gone, raise the weather curve a degree or two, or give the living room more radiator. A second radiator there makes more sense than one in the conservatory if that's the room you want warm. Whether the living room radiator is big enough for that room shows in a room-by-room heat loss calculation, which you can do yourself now the installer is gone. This is the one I did for my own house: https://heatlosspro.cloud/s/YAzppFumRwF3TzRGRBaV0g. If you draw yours, post the link here and I'll go through it with you, which rooms fall short and by how much.
 
Thank you mk321123,

I've discovered, come to realise that it's happening most often, in fact every time at some point in the early hours every morning after a temperature setback perhaps. Because the bedroom is far too warm for me i set back the temperature about 3 degrees at 9pm. An hour and a half'ish+ before i go to bed. I open the bedroom window to help cool down the room too. sometimes i get up to find the heatings gone off, or sometimes after a short while after turning up the room-stat in the morning it goes off.

Also worth noting that thinking about things when i'm away for the weekend i turn down the room-stat a good few hours before i leave, theirs no setback taking place overnight fri, sat and sun and the heating doesn't go off over the weekend. On a Monday i'll turn the room-stat up and sometimes the heating will go off later in the morning, not every time though.

It's a 4kw system with a water flow of usually around 12L/m. This flow reduces to 7.5L/m sometimes and as low as 5L/m on occasions.

The control unit says the temp difference between flow and return is about 5 degrees, it varies a little but no more than about 1/2 degree maybe a tad more on occasions.

I had actually thought about adding a radiator in the living room with idea that i would then get away with turning the radiator in the bedroom down, even possibly off! The system was designed with the knowledge that i would be adding another radiator later, later never happened. Installer made it clear that the system would handle another radiator without issues.

Installer's still helpful and i've found i can call them for advice, they say they are installers only albeit they will always attend an installation whilst it's under warranty. The chap who's been servicing it won't do anything other than service it because he says he didn't install it.

I've a service booked for mid December, i'll ask him about filters etc and prompt him to check them for me.

Which IR thermometer would you recommend to purchase, something that's good value but not too expensive as i'll probably never use it again? I'll enquire if it's possible to hire one from my local tool hire centre.

additionally thank for your offer of further help, i'll have a look at this next week.
 