I have an ASHP. All main pipe rums are 22mm, all radiators are oversized, standard and new.
The position of the radiators in relation to the pump means that the nearest rads in bedrooms upstairs are fed first and these rooms are overheating (For Me) i prefer a cooler bedroom. The rads furthest away are in the kitchen and living room. The system is struggling to warm up these two rooms.
If i turn down the temperature using the TRV's in the bedrooms the system complains and switches itself off (Too low water flow).
I'm thinking it may improve things if i can connect up the Kitchen and Living room radiators without stepping down the pipe size from 22mm to 15mm before connecting to the radiators.
Is this a worthwhile idea, and if it is can you get valves that allow the direct connection of 22mm pipes to std modern radiators. Would it improve water flow to these two radiators sufficiently so that i can turn down the rads in the bedrooms so that i can get a good nights sleep and have a warmer living room?
Or would it be a better idea to add another radiator to the living room? When the system was installed, the installer said that when i get the conservatory roof changed to an insulated roof (Done) the system will cope with an added radiator in the conservatory when i'm ready but instead would it be better to add another radiator to the living room to increase flow, increase warmth to that room and turn down rads in bedrooms?
The position of the radiators in relation to the pump means that the nearest rads in bedrooms upstairs are fed first and these rooms are overheating (For Me) i prefer a cooler bedroom. The rads furthest away are in the kitchen and living room. The system is struggling to warm up these two rooms.
If i turn down the temperature using the TRV's in the bedrooms the system complains and switches itself off (Too low water flow).
I'm thinking it may improve things if i can connect up the Kitchen and Living room radiators without stepping down the pipe size from 22mm to 15mm before connecting to the radiators.
Is this a worthwhile idea, and if it is can you get valves that allow the direct connection of 22mm pipes to std modern radiators. Would it improve water flow to these two radiators sufficiently so that i can turn down the rads in the bedrooms so that i can get a good nights sleep and have a warmer living room?
Or would it be a better idea to add another radiator to the living room? When the system was installed, the installer said that when i get the conservatory roof changed to an insulated roof (Done) the system will cope with an added radiator in the conservatory when i'm ready but instead would it be better to add another radiator to the living room to increase flow, increase warmth to that room and turn down rads in bedrooms?