It's a 4kw system with a water flow of usually around 12L/m. This flow reduces to 7.5L/m sometimes and as low as 5L/m on occasions.
The control unit says the temp difference between flow and return is about 5 degrees, it varies a little but no more than about 1/2 degree maybe a tad more on occasions.
You probably know this anyway from the display :
If the output is 4.0kW at 12LPM, then the dT is, 4.0*860/60/12, 4.78C, as reported by the control unit.
A flowrate of 7.5LPM (at a 5C dT) outputs, 7.5*60*5.0/860, 2.62kW
A flowrate of 5.0LPM (at a 5C dT) outputs, 5.0*60*5.0/860, 1.74kW