Where are these auto-fillers I keep reading about? I've never seen one for sale or installed.

Can someone provide a link please?

Ta
 
Sponsored Links
do they comply with water byelaws? If you have a leak on a sealed system they how will you find out until the ceiling collapses or your metered water supply bill comes in at a massive amount! Are these really such a good idea?
 
Sponsored Links
I'm sure they don't meet UK water regs.

Its just a PRV and an NRV.

Water regs say there has to be an air gap, thus auto refillers over here typically have a break tank and pump.

I think Mikrofill have another patented way of doing it too.
 
I came across a clever one in a rented flat two weeks ago.

It has no filling loop but instead a knob valve, a solenoid valve and a pressure switch.

It only fills when the knob valve is opened and the solenoid is only open until the pressure reaches one bar.

So the tenant cannot overfill !

The Bangladeshi landlord has 240 properties and must save thousands on repairs with the benefit of that little device costing about £35 installed per boiler.

Tony
 
usually if i can i use a standard prv set at 1 bar fit it on the filling loop, so instead of running up and down stairs every couple of minutes refilling the system i can leave the filling loop open.
 
Where are these auto-fillers I keep reading about? I've never seen one for sale or installed.

Can someone provide a link please?

Ta

http://www.arrowvalves.co.uk/productdetail.php?id=2

I'm fairly certain the one posted by Planet Thanet doesn't comply with UK Water Regulations, but can't be bothered to look it up. Not sure whether a double check valve is still legal for houses.

The Arrow Valves job is a type BA back-flow prevention device, with a reduced pressure zone valve to prevent back-siphonage of Category 4 fluid into the water mains. It should be installed and commissioned by a competent person.

Pressurization units have a break tank (type A air gap), a pumps to pump water into the system and high and low pressure switches.

If you intend to fit any one of these to top-up a leaking system, the problem will multiply a hundred-fold and will haunt you forever.
 
They come as standard on the Gledhill Gulfstream boiler/unvented tank!!!!

Seems like a good idea, does away with end users running the system dry after bleeding a system, however does away with pumping over and drawing air.
 
Hi

Wasn't sure that was the product Elite Heat was after.
Now I know it is I would agree that it is a potential nighmare if the system has a leak. I wouldn't fit one.
AFAIK double check is approved for domestic.

Thanet.
 