I have just bought a used bandsaw which needs a 16A supply - the guy who owned it before me had a dedicated 16A connection for it.
I have a 32 amp supply running from my house consumer unit to my garage, where the saw will be used. In the garage there is a separate consumer unit with B32 and B16 circuit breakers.
I have wired it to the B16 circuit breaker, but it trips it straight out when I turn the saw on. I then connected it to the 32A circuit breaker and it worked OK.
I want to add a dedicated circuit breaker for the saw, but am not sure what circuit breaker to add. Should it work off a 16 (could there be some fault with the saw, or that circuit breaker, causing it to trip), or is there likely to be some sort of 'surge' that occurs just as the saw is powered on meaning it needs a higher circuit breaker value?
Also, I heard there are different type's of breaker - B type, C type etc. Is it correct to use the 'B' type in this case?
I have a 32 amp supply running from my house consumer unit to my garage, where the saw will be used. In the garage there is a separate consumer unit with B32 and B16 circuit breakers.
I have wired it to the B16 circuit breaker, but it trips it straight out when I turn the saw on. I then connected it to the 32A circuit breaker and it worked OK.
I want to add a dedicated circuit breaker for the saw, but am not sure what circuit breaker to add. Should it work off a 16 (could there be some fault with the saw, or that circuit breaker, causing it to trip), or is there likely to be some sort of 'surge' that occurs just as the saw is powered on meaning it needs a higher circuit breaker value?
Also, I heard there are different type's of breaker - B type, C type etc. Is it correct to use the 'B' type in this case?