I have a Baxi 80e combi boiler and the hot water will not fire unless the tap is turned on full. Central heating works fine. Any suggestions??
 
Sponsored Links
Anyone care to expand on this a little?

I have exactly this problem. Is there something I can adjust?

thanks,
J.
 
Sponsored Links
The diaphragm is a rubber seal that fits inside the pressure differential assembly.
It pushes a pin onto the microswitch when you turn on the hot water.
If it has a hole in it it may be sruggling to push the pin all the way until you turn the water on full and provide more pressure.
You can get a diphragm for a tenner, I bought one off ebay the other week.
http://cgi.ebay.co.uk/BAXI-80E-105E...photoQQcmdZViewItemQQ_trksidZp1742.m153.l1262

For a diagram of where it fits go to http://www.partsarena.com/baxi/ and browse to baxi/boiler/combi/combi 80E/parts list/combi 80e/HYDRAULICS.
The hot water diaphragm is located in part 103, pressure differential assembly.
 