Baxi Solo 2 50pf ignition
R
ringy1
Hi my baxi solo 2 50pf boiler when turned on takes ages to fire up. It can spark upto 30 time before the pilot lights? Is there something wrong with it or is this normal? if i turn the boiler off and turn back on straight away the pilot lights straight away. Is a part failing?
R
ringy1
It only takes ages for the pilot to light when the boiler has not being turned on in a good while but if i turn it off and then turn it back on the pilot lights straight away must be the gas valve sticking. Ill change that :D Thanks for the heads up
26 Jun 2004
London
As you are not gas registered then you should not be touching any gas carying parts as you well know!
G
gaswizzard
You go ahead and waste yer money. :D
24 Jul 2003
London
YOU said it was the gas valve - nobody else did.
I can think of 3 other things more likely.
Don't forget to adjust the gas valve properly and check the flue gas analysis after, or you might wreck your boiler, burn your house down, die, and that.
Now I've thought of another 3...
R
ringy1
I have cleaned and checked the electrode and checked gap (3mm) I have checked the injector is not blocked. solenoid is good 5 K OHM. Im getting 230v to gas valve. I then connect a manometer to inlet test point to gas valve let in 20mbar of gas and turned off ECV and turned on boiler and my manometer did not drop. Looks like i am right ;)
14 Mar 2010
Norfolk
Then go ahead and change the valve if you feel lucky. Better still get someone who knows what they're doing, to ensure your safety.
R
ringy1
Changed gas valve, working perfect now. Checked burner pressure 16mbar (within range) and i also did a let by and tightness test after. All good :D Thanks for all your help lads ;)
19 Aug 2008
Essex
Hey OP how many boilers have you got. You appear to have also "worked" on a Vokera Linea and a Potty Profile 50?
Unless of course you live in a large property/have a second home/swimming pool etc?