Boiler is an Ecotec Plus 831.
House is a smallish 4 bed 1920s semi. 10 rads (counting the 3 small ones round a bay as 1). No huge radiators. Pipework mainly 22mm and 15mm copper. Some plastic.
Fair bit of boiler work done recently:
1. New heat exchanger.
2. New pump.
3. Some internal pipes he said (flexible pipe?)
4. He repressurised the Pressure Vessel.
Before this I used to keep an eye on the system pressure. If the display was showing 65deg (flow temp) but the pump and flame weren't on, then the pressure would always increase by 0.2bar when they did come on.
Now I'm getting a difference from 'off' to 'on' of about 1.1 bar.
Just now I turned it off. Let it cool down to about 40deg. Pressure went to 1.0 bar. Turned it back on waited for it to get to 75 deg. Pressure was 2.1
Is that sort of difference OK? The digital and analogue sensors agree with each other.
One thing I've noticed is that the return temp isn't cold enough. If the flow is 75deg, the return is 68 deg. So it looks like I've got some work to do balancing the radiators to slow the flow down.
Thanks.
House is a smallish 4 bed 1920s semi. 10 rads (counting the 3 small ones round a bay as 1). No huge radiators. Pipework mainly 22mm and 15mm copper. Some plastic.
Fair bit of boiler work done recently:
1. New heat exchanger.
2. New pump.
3. Some internal pipes he said (flexible pipe?)
4. He repressurised the Pressure Vessel.
Before this I used to keep an eye on the system pressure. If the display was showing 65deg (flow temp) but the pump and flame weren't on, then the pressure would always increase by 0.2bar when they did come on.
Now I'm getting a difference from 'off' to 'on' of about 1.1 bar.
Just now I turned it off. Let it cool down to about 40deg. Pressure went to 1.0 bar. Turned it back on waited for it to get to 75 deg. Pressure was 2.1
Is that sort of difference OK? The digital and analogue sensors agree with each other.
One thing I've noticed is that the return temp isn't cold enough. If the flow is 75deg, the return is 68 deg. So it looks like I've got some work to do balancing the radiators to slow the flow down.
Thanks.