Boiler firing even though zones all off

Discussion in 'Plumbing and Central Heating' started by Deansplit, 9 Dec 2019.

  1. Deansplit

    Deansplit

    Joined:
    5 Oct 2005
    Messages:
    576
    Thanks Received:
    2
    Country:
    United Kingdom
    I have a closed heating system with 6 motorised valves to zone the rooms/areas plus a heat leak (two 1” vertical pipes are joined by 15mm pipes). I noticed recently boiler continually firing up for a minute or so even though all zones had reached temperature and to double check I turned all zones off and it still happened. So sounds like the boiler is just heating the water in the heat leak - is this a fault with the pump ie. it’s not switching off therefore as soon as the heat leak water cools it fires the boiler?

    Thanks for any advice
     
  2. Sponsored Links
  3. fezster

    fezster

    Joined:
    30 Jan 2013
    Messages:
    528
    Thanks Received:
    60
    Location:
    London
    Country:
    United Kingdom
    If your boiler is fired by the SL (orange wire in honeywell 2 port valves) in the motorised valves, it's possible one of the microswitches is sticking. This is quite a common fault.
     
    • Thanks Thanks x 1
  4. Deansplit

    Deansplit

    Joined:
    5 Oct 2005
    Messages:
    576
    Thanks Received:
    2
    Country:
    United Kingdom
    Thanks Fezster - so how do I check this? Would that not mean the valve at fault would be stuck on open so therefore the rads are always on (which they're not)?
     
  5. imiller9

    imiller9

    Joined:
    7 Jun 2009
    Messages:
    42
    Thanks Received:
    8
    Location:
    Liverpool
    Country:
    United Kingdom
    No, the valves have a permanent 240v feed to them and if the switch is stuck it will pass that voltage onto your boiler without the valve to physically open.
     
    • Thanks Thanks x 2
  6. fezster

    fezster

    Joined:
    30 Jan 2013
    Messages:
    528
    Thanks Received:
    60
    Location:
    London
    Country:
    United Kingdom
    It's easy to check with a multimeter and access to the wiring centre.

    However, if you're not confident in doing so (as there will be live electricity flowing when doing the check) then better to call somebody in.
     
    • Thanks Thanks x 1
    • Like Like x 1
  7. Deansplit

    Deansplit

    Joined:
    5 Oct 2005
    Messages:
    576
    Thanks Received:
    2
    Country:
    United Kingdom
    This is fine, have done lots of wiring in the past and have a very good multimeter. But is it easy enough to explain exactly how I go about checking? The pump is constantly on and very hot unless I physically switch the boiler off so I presume I need to sort this ASAP for fear of damaging the pump?
     
  8. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    21,499
    Thanks Received:
    8,376
    Location:
    Lanarkshire
    Country:
    United Kingdom
    inside the wiring center there will be a grey wire for each valve all connected together, these have a permanent live connected, there will be an orange for each valve and these will all be connected and will be connected to the switched live at the boiler, with everything switched to off (not the fused spur) test for live at the terminal with the orange wires, if there is live there, you need to turn off the power and seperate all the orange wires and test for continuity one at a time with the grey wires, when you find which one has continuity trace that one to which valve it is from and change the actuator
     
    • Thanks Thanks x 1
    • Like Like x 1
  9. fezster

    fezster

    Joined:
    30 Jan 2013
    Messages:
    528
    Thanks Received:
    60
    Location:
    London
    Country:
    United Kingdom
    Just to add to ianmcd's comprehensive post above, you may find if you activate and deactivate the microswitch a few times, it becomes unstuck (assuming that is the fault). Might be worth trying before ordering a new actuator.
     
    • Thanks Thanks x 2
  10. Sponsored Links
  11. Deansplit

    Deansplit

    Joined:
    5 Oct 2005
    Messages:
    576
    Thanks Received:
    2
    Country:
    United Kingdom
    Thanks but this would surely mean the rads of that zone would be getting heat?
     
  12. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    21,499
    Thanks Received:
    8,376
    Location:
    Lanarkshire
    Country:
    United Kingdom
    No, you misunderstand how the valve works, when asked to heat the zone, the valve motor is powered, this opens the valve to allow the flow of water to that zone, once the valve is fully open, this makes the micro switch , this tells the boiler and pump to operate, when that zone is satisfied the power to the motor is stopped so the spring return mechanism closes the valve, then the micro switch should go open circuit and stop the boiler from firing, but the switch is sticking but the valve is closing, so the boiler still fires but the valve is closed so the heat has no where to go so the boiler gets hot too quickly and shuts down, then cools and starts heating again
     
  13. Deansplit

    Deansplit

    Joined:
    5 Oct 2005
    Messages:
    576
    Thanks Received:
    2
    Country:
    United Kingdom
    OK thanks for the detailed explanation, that helps :) Soooo, is the faulty one's switch is now on forever (or until freed up or replaced) or if I switch the fused spur off, will it reset, in which case, if it does I could test each MV one by one by switching it on and seeing how the boiler runs? Think you're going to say no, but just though of an easy way to check if this is the case.
     
  14. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    21,499
    Thanks Received:
    8,376
    Location:
    Lanarkshire
    Country:
    United Kingdom
    I have already told you how to test it, not rocket science, if you are unable to do that it is time to get someone in
     
  15. Deansplit

    Deansplit

    Joined:
    5 Oct 2005
    Messages:
    576
    Thanks Received:
    2
    Country:
    United Kingdom
    Yes, and in theory that's easy to test but as you can see, it's not as clear as you've described...
     

    Attached Files:

  16. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    21,499
    Thanks Received:
    8,376
    Location:
    Lanarkshire
    Country:
    United Kingdom
    yes it is , turn the power off and pull everything out and spread all the connections
     
    • Thanks Thanks x 1
  17. Deansplit

    Deansplit

    Joined:
    5 Oct 2005
    Messages:
    576
    Thanks Received:
    2
    Country:
    United Kingdom
    Sorted this today :) And delighted that when I took it apart rather than just buying a new one, that I saw lots of plastic had worn off to the metal ring which has the cogs on... scraped this off and bingo, works a treat ;)
     
  18. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page