Boiler intermittent fault

Joined
20 Mar 2018
Messages
4,389
Reaction score
910
Location
Stoke-on-Trent
Country
United Kingdom
I have an old Ideal SE50 which has an intermittent fault.

The burner sometimes fails to light, though the fan is running. I turn the control-stat down to minimum then back up, and it then fires, each time it's happened so far. It seems to be more likely to happen when calling for HW (it's a W-plan) though I can't see why that would make a difference.

I'm inclined to suspect dirty contacts in the control-stat. Can anybody please comment or think of any other explanation?
 
Within the PCB?
As a stopgap, and to see if it happens on CH, I've turned the cylinder-stat down to zero and switched the immersion on.
No, either motorised valve, cylinder stat or programmer
 
That test told you plenty. Moving the dial makes it fire, so the stat still works somewhat. Dirty contacts make total sense for an older boiler.

Try this before spending money on parts. Kill the power. Pop the cover and check those contacts. If they look pitted or black, clean them with fine emery paper. Takes five minutes and costs zero. I fixed two old stats this way.

Check the cylinder stat, too. On a W-plan setup, hot water runs right through it. If this only happens during a hot water call, that stat might be dying. They fail without making a sound.
 