I have a Ravenheat 820/20T boiler that is outputting only 13 to 16kW on domestic hot water, whereas its supposed to do about 23kW. This means the hot water isn’t hot enough for the wife’s shower, especially in the winter when the incoming water is a bit colder.
I’ve checked the voltage at the gas valve's modulation/solenoid coil terminals and when in domestic water mode its either 0V or 24V depending on the position of the DHW thermostat. I guess it doesn’t do continuous variable control as it won’t do anything other than 0V or 24V. Maybe it should since it has a thermostat dial.
Curiously when in central heating mode it only reads either 0V or 12V depending on the position of the CH thermostat.
From this I guess the boiler does lo-mid-hi fire mode 0V-12V-24V.
At 0V across the modulation coil it heats 6.5litr/min from 10C to 40C (13kW)
At 24V across the modulation coil it heats 6.5litre/min from 10C to 45C (16kW)
I have no idea what it’s heat output is in central heating mode, but it keeps the house warm enough. The flame height seems no greater than in DHW mode.
I’ve adjusted the fuel pressure gizmo on the end of the modulator coil and sometimes get 50C out but not consistently. I may need to put the setting back however as the pilot seems to go out since. Guess it’s lifting the pilot flame off its burner.
I’ve checked for heat exchanger performance by measuring flue gas temperature, it reads 150C, that’s about normal for a non-condensing combi so my heat exchanger shouldn’t be fouled or blocked as I’m recovering all the heat.
Since I don’t get full output even when 24V on the gas valve I assume the fault is with a component associated with it. Or a fuel pressure / restriction issue.
Anybody suggest what the problem might be?
I’ve checked the voltage at the gas valve's modulation/solenoid coil terminals and when in domestic water mode its either 0V or 24V depending on the position of the DHW thermostat. I guess it doesn’t do continuous variable control as it won’t do anything other than 0V or 24V. Maybe it should since it has a thermostat dial.
Curiously when in central heating mode it only reads either 0V or 12V depending on the position of the CH thermostat.
From this I guess the boiler does lo-mid-hi fire mode 0V-12V-24V.
At 0V across the modulation coil it heats 6.5litr/min from 10C to 40C (13kW)
At 24V across the modulation coil it heats 6.5litre/min from 10C to 45C (16kW)
I have no idea what it’s heat output is in central heating mode, but it keeps the house warm enough. The flame height seems no greater than in DHW mode.
I’ve adjusted the fuel pressure gizmo on the end of the modulator coil and sometimes get 50C out but not consistently. I may need to put the setting back however as the pilot seems to go out since. Guess it’s lifting the pilot flame off its burner.
I’ve checked for heat exchanger performance by measuring flue gas temperature, it reads 150C, that’s about normal for a non-condensing combi so my heat exchanger shouldn’t be fouled or blocked as I’m recovering all the heat.
Since I don’t get full output even when 24V on the gas valve I assume the fault is with a component associated with it. Or a fuel pressure / restriction issue.
Anybody suggest what the problem might be?