Hi, hopefully I can get some advice.
My central heating boiler, Potterton Prima Profile 60E, keeps tripping on overheat. This is very regular, a lot of mornings the heating isn’t on because it tripped the night before.
The system is s(?) plan, two motorised valved.
I have checked the bypass valve (15mm gate) and it is well open and I have proved a flow.
This evening I did a few tests.
I wound the thermostat up on both the hot water tank and the boiler and started the hot water system up.
With the boiler very hot and still firing I shut off the program and the following happened.
1, Boiler shutdown (HW valve shuts), pump stops, boiler trips, pump starts on overrun.
2, Boiler shutdown (HW valve shuts), pump stops, boiler trips, pump does not start.
3, Boiler shutdown (HW valve shuts), pump stops, pump starts on overrun, boiler trips.
4, Boiler shutdown (HW valve shuts), pump continues on overrun, boiler trips.
The instructions say the pump overrun will initiate if the water is >80C. They do not state what temp the boiler will trip at although they state max temp is 82C.
My thoughts:
The trip temp and overrun temp are too close together meaning that if the HW valve closes and the boiler shuts down while it is near it’s upper temp range the boiler temp increases to trip temp before the overrun can cool it.
Can the overrun thermostat temp ‘drift’ if the thermostat is old, is this how they fail or would it just not work at all.
Either it’s this thermostat or a fault in the design with the overrun not allowing enough flow, being only 15mm.
Or am I way off the mark?
My central heating boiler, Potterton Prima Profile 60E, keeps tripping on overheat. This is very regular, a lot of mornings the heating isn’t on because it tripped the night before.
The system is s(?) plan, two motorised valved.
I have checked the bypass valve (15mm gate) and it is well open and I have proved a flow.
This evening I did a few tests.
I wound the thermostat up on both the hot water tank and the boiler and started the hot water system up.
With the boiler very hot and still firing I shut off the program and the following happened.
1, Boiler shutdown (HW valve shuts), pump stops, boiler trips, pump starts on overrun.
2, Boiler shutdown (HW valve shuts), pump stops, boiler trips, pump does not start.
3, Boiler shutdown (HW valve shuts), pump stops, pump starts on overrun, boiler trips.
4, Boiler shutdown (HW valve shuts), pump continues on overrun, boiler trips.
The instructions say the pump overrun will initiate if the water is >80C. They do not state what temp the boiler will trip at although they state max temp is 82C.
My thoughts:
The trip temp and overrun temp are too close together meaning that if the HW valve closes and the boiler shuts down while it is near it’s upper temp range the boiler temp increases to trip temp before the overrun can cool it.
Can the overrun thermostat temp ‘drift’ if the thermostat is old, is this how they fail or would it just not work at all.
Either it’s this thermostat or a fault in the design with the overrun not allowing enough flow, being only 15mm.
Or am I way off the mark?