Quite, that's what I assumed, and I agree totally that it is the common sense approach.Simple answer - never.In real-world terms, I wonder how often any of this really gets taken into account in domestic premises, particularly given that boxing is very often 'retrofitted' after the electrical installation has been designed and installed
As I said, I personally agree that this is the common sense approach. However, in many people's eyes the name of the game is unfortunately not 'common sense' but, rather, 'compliance with the regulations'.This isn't usually a problem, since most circuits in a house will never be used at anything like their maximum capacity, and for many circuits the cables are substantially oversized.
In terms of the regs, the problem with the common sense approach is obviously that it is taking account of how much load the circuits/cables really are likely to bear in practice, whereas 5.1.1 & 5.1.2 of Appendix 4 of the regs seem to make it pretty clear that they are expecting the required cable size to be determined on the basis of the rating of the overload protection device protecting the cable concerned (or of each and all the cables concerned, when grouped), which will obvioulsy often be a lot more than the common sense estimate of load.
It therefore strikes me that most people are being sensible, but ignoring the word of the regs - which is a slightly odd situation!
Kind Regards, John.