Installation methods for cable

Joined
7 Feb 2006
Messages
27
Reaction score
0
Location
Leeds
Country
United Kingdom
Hello

This is a general question on cable installation methods:

I have a 6mm hituf cable running through a wall from inside to outside. A want to check the current carrying capacity so looking at installation methods (BS7671) that appears to be method 1 embedded directly in masonry.... Also Clipped direct is method 1 which confuses me.

If I refer to my table (4D2A) I'm assuming I take the column headed Reference method 1 (clipped direct) although it makes no reference to embedded directly in masonry.

I'm probably being stupid so if someone could clarify I'd greatly appreciate it.

Cheers
 
Sponsored Links
C'mon lads/lassies I know your looking, where's 'ban all sheds' when you need him??
 
That's a shame I'll miss his argumentative nature?

Anyway Steve can you guide me?
 
Sponsored Links
It's do with heat dissipation of the cable which would be the same for cable buried in masonry or clipped direct for that particular cable.
 
Hi DESL

Many thanks I was just confused by the table heading. Cheers
 