if you wanted to alter the pipes the cold feed tee should be relocated just above the vent tee to a max of 6inch . when you take that compression tee off you will see a partial blockage which is causing the problem , there will be a similar restriction at the vent tee which could be cleared bye poking if you wasnt renewing that . add sentinal x100 when refilling
keep the vent in the same position and lower the feed to suit . the distance from pump is not that important .if you wanted to alter the pipes the cold feed tee should be relocated just above the vent tee to a max of 6inch . when you take that compression tee off you will see a partial blockage which is causing the problem , there will be a similar restriction at the vent tee which could be cleared bye poking if you wasnt renewing that . add sentinal x100 when refilling
So a maximum of 6 inches between expansion and feed. But how far should the feed be away from the pump?
The distance between the Feed and Vent isn't that critical. What you have to avoid is a pressure difference between them, due to a blockage as I showed.
In your case it's simple because you have a compression joiunt. Undo it and clear out the blockage!
You don't need to move any pipes.
I expect the pipes in the compression tees have lovely burrs on them - you could scrape those out to discourage further scale collection.