According to the data sheet in front of me :-
Magnetic trip -
Type 1 (Grey handle) 2.7 - 4 x In
Type 2 (Green handle) 4 - 7 x In
Type 3 (Orange handle) 7 - 10 x In
Type 4 (Black handle) >10 x In
SP MCBs have the following fault ratings:-
5A to 20A = 6kA 25A to 60A = 5kA 80 to 100A = 3kA
Triple pole 10A to 60A = 5kA 80A to 100A = 3kA
As for the RCBOs:-
Max Zs 1666 ohms and fault rating 2kA
This is from the original Federal literature. I have the time/current graphs here as well if you get really desperate.