How would you approach the following (I'm interested both from a theory and practical point of view as I'm studying for 2382 and working out an actual design spec prior to LAB submission right now):
Lighting circuit with mixture of
6 x GU10 w. 11WCF
3 x GX10 HID (Britespot 35w Metal Halide).
Ususally I understand (irrespective of the lamp holder and ignoring diversity for now (see last questions below)) a minimum of 100W per lamp should be assumed i.e. 9 x 100w = 900w / 230 = 3.91A.
What happens when you mix in HID though?
I think I am right in saying that (assuming power factor is not <0.85), the guideline is to assume a 1.8 correction for transient load i.e. on the 35w/ 100v HIDs above this would be (3 x (35w*1.8))/100 = 1.89A.
However, when you think about it, the 100w guideline assumes 230v i.e. 0.43A per lamp. At 100v (which is what the balasts run at), the same calculation produces 0.63A - a 43% difference.
I've searched everything I can think of, but can't see a guide on this.
I suppose a second related question is whether the Design Current for a lighting circuit can take account of the type of lamp holder in use (for example, while a GU10 can take anything upto a 100W GU10, a GX10 can only take a 35W Sylvania HID. If this was the case then the Design calc could use the actual I guess.
Also, if this is a single radial supplying all of these lights in the same room, am I right in saying that it is not appropriate to apply 66% diversity guideline as it is likely they will be used simultaneously.
Apologies for the long post, hopefully someone will have experience on this.
Lighting circuit with mixture of
6 x GU10 w. 11WCF
3 x GX10 HID (Britespot 35w Metal Halide).
Ususally I understand (irrespective of the lamp holder and ignoring diversity for now (see last questions below)) a minimum of 100W per lamp should be assumed i.e. 9 x 100w = 900w / 230 = 3.91A.
What happens when you mix in HID though?
I think I am right in saying that (assuming power factor is not <0.85), the guideline is to assume a 1.8 correction for transient load i.e. on the 35w/ 100v HIDs above this would be (3 x (35w*1.8))/100 = 1.89A.
However, when you think about it, the 100w guideline assumes 230v i.e. 0.43A per lamp. At 100v (which is what the balasts run at), the same calculation produces 0.63A - a 43% difference.
I've searched everything I can think of, but can't see a guide on this.
I suppose a second related question is whether the Design Current for a lighting circuit can take account of the type of lamp holder in use (for example, while a GU10 can take anything upto a 100W GU10, a GX10 can only take a 35W Sylvania HID. If this was the case then the Design calc could use the actual I guess.
Also, if this is a single radial supplying all of these lights in the same room, am I right in saying that it is not appropriate to apply 66% diversity guideline as it is likely they will be used simultaneously.
Apologies for the long post, hopefully someone will have experience on this.