Central heating doesn't appear to be a closed system

Joined
19 Jul 2023
Messages
4
Reaction score
0
Country
United Kingdom
Hi there,

I have a query that has confused my limited knowledge of plumbing. I have moved into a new house where the radiators connected using copper microbore pipping. Each radiator has been connected separately to the main pipes running from the combi boiler in the loft. I needed to remove a radiator off the wall for replastering and as there appeared to be nowhere to drain the system, we disconnected a radiator and collected the water leaking out – this appeared to be predominantly from the radiator itself and looked like it had the rust additive in it – no water came out from the piping itself. Presumed this was fine, however later on when using the hot water tap in the kitchen, clear water started coming out of the piping where the radiator had been removed.

I can’t understand why this happens as I presumed that it would be a closed system, so failing to understand why it is affected by using the tap. I have since put the radiator back on, as 8mm stop ends I purchased failed to fit onto the microbore pipe ends. I wonder if it was caused by air getting into the system from the open pipes, and it emptied the remaining water in the system, but then this doesn't explain why the water that came out was clear and didn't have the addative in it.

So I’m wondering if anyone can help advise firstly why this is happening and secondly, how is the best way to go about removing radiators as I require these to eventually be removed in all the rooms.



Many thanks
 
so you never turned the valves off to the rad and wondered why water came out when the pump kicked in for HW
 
so you never turned the valves off to the rad and wondered why water came out when the pump kicked in for HW
I mean this is probably a daft question but are the HW and central heating not separate and separate pumps? I don't understand if it's a closed system why running the HW would pump HW into this system?

Where would the shut off valves be to the radiators, as I couldn't locate them
 
I mean this is probably a daft question but are the HW and central heating not separate and separate pumps? I don't understand if it's a closed system why running the HW would pump HW into this system?

Where would the shut off valves be to the radiators, as I couldn't locate them
on the actual radiator put a pic up of your rad
 

Attachments

  • PXL_20230719_172956438.jpg
    PXL_20230719_172956438.jpg
    233 KB · Views: 67
  • PXL_20230719_173001300.jpg
    PXL_20230719_173001300.jpg
    224.1 KB · Views: 72
  • PXL_20230719_173006697.jpg
    PXL_20230719_173006697.jpg
    278.5 KB · Views: 84
You close both valves on the rad ,remove the rad after draining it, and fit blanking cap nuts to both valves.
No need to remove the valves from the pipework.
 
I mean this is probably a daft question but are the HW and central heating not separate and separate pumps? I don't understand if it's a closed system why running the HW would pump HW into this system?

Where would the shut off valves be to the radiators, as I couldn't locate them
It’s a combi boiler, so usually just the one pump. The heating and hot water remain separate circuits, so as not to drink heating water, but the boiler uses the heating water to heat the hot water, which circulates around a heat exchanger then a secondary heat exchanger (usually).
 