I have an Ariston Clas HE EVO System boiler. Over the last few months, getting on for a year, the sytem loses pressure. Not regularly or constantly. It was working ok for weeks, months and then when I get up in the morning pressure would be a zero. This is getting more frequent. I repressurize, check everyday and there would be no change then suddenly, zero. I never seem to catch it half way. The pressure regulator has 1.4 bar when the system is at zero and I tied a bag onto the relief valve discharge and it is empty. I can't see any leaks from the boiler. It takes minimum input to repressurize. It is an old house, radiator pipes are under the floors and hard to get to. I've had a quick look and can't see anything.
So question is how do I find the leak location? Although the boiler looks ok, the fact that the everying works, then suddenly the pressure drops and recharging is a minimum amount, makes me think it is something getting switch on/off and leaking at one position. The zone valves are under the boiler and easy to see and there are no leaks there. When the central heating was on, all radiators were hot right to the top, no air trapped. And if it is the radiator pipes, is there a quick way to identify where the leak is?

Any suggestions welcomed.
 
Presumably in this weather you are only heating the HWC therefore the radiators are isolated at the motorised valve. This suggests that the "leak" is somewhere in the boiler or the hot water circuit.
 
I have an Ariston Clas HE EVO System boiler. Over the last few months, getting on for a year, the sytem loses pressure. Not regularly or constantly. It was working ok for weeks, months and then when I get up in the morning pressure would be a zero. This is getting more frequent. I repressurize, check everyday and there would be no change then suddenly, zero. I never seem to catch it half way. The pressure regulator has 1.4 bar when the system is at zero and I tied a bag onto the relief valve discharge and it is empty. I can't see any leaks from the boiler. It takes minimum input to repressurize. It is an old house, radiator pipes are under the floors and hard to get to. I've had a quick look and can't see anything.
So question is how do I find the leak location? Although the boiler looks ok, the fact that the everying works, then suddenly the pressure drops and recharging is a minimum amount, makes me think it is something getting switch on/off and leaking at one position. The zone valves are under the boiler and easy to see and there are no leaks there. When the central heating was on, all radiators were hot right to the top, no air trapped. And if it is the radiator pipes, is there a quick way to identify where the leak is?

Any suggestions welcomed.
You say it takes minimum input to repressurize it.
If you have say a 10L EV (expansion vessel) that might normally be pre charged to 1.0bar and you then charge it to 1.4bar, then that will take 1.67L to do so which means that you are possibly losing/leaking 1.67L each time the boiler pressure falls to zero but you would normally take ~ maybe over a minute or so to do this except you fully open the filling valve. If the pre charge pressure is 1.4bar then it will only require a few ml of water, say 0.2L or less to recharge it so you may have no leak.
Assuming the boiler pressure is 1.4bar cold, what is it after doing a HW cylinder re heat?

Suggest checking /get checked the EV pre charge pressure as a start + the air vent as suggested above.
 