Hi everyone i am in need of some help I have flushed my heating system with with sentenal 800. Ileft it in for a week then flushed it out till water ran clean then added x100.I now have hot rads upstaires cold downstaires. so i was thinking could i use hydrocloric acid if its ok how long do i leave it in thanks in advance
 
Have you checked the pump,
Have you turned the upstairs rads off to see if lower circuit clear (or not)?
 
check the pump is turning.
If the boiler is short cycling from first turn on. It inidicates the pump isn't moving the water. Could be a blockage/air lock also.
You don't say if the system worked before.
 