This is not a condensing junior. It was installed sept 04. The HW works fine but on the CH side when a demand is created it takes about 10 to 12 mins to get up to temp( all rads get hot, actually only 5 rads) then kettling occurs in the ~HX the O/H stat kicks in and shuts the gas valve and the auto air vent opens.
The pump works , the primary CH ensor tested OK and was even replaced but still no joy, Just wondering whether its scaling in the HX or a control boar problem but everything seems ok on the control board. If its scaling on the HX why isn't it causing a problen on the HW side? When the boiler was replaced I don't know if the rads where flushed or cleaned so maybe it is FeO2 deposits rather than scale so causing the problem on the CH side and not the HW?
Any advice appreciated.
Oh I forgot to add, gas valve is modulating ok, when demand is created it goes up to min and after a set time ramps up to the setting in the Mis, just doesn't modulate down before kettling occurs.
The pump works , the primary CH ensor tested OK and was even replaced but still no joy, Just wondering whether its scaling in the HX or a control boar problem but everything seems ok on the control board. If its scaling on the HX why isn't it causing a problen on the HW side? When the boiler was replaced I don't know if the rads where flushed or cleaned so maybe it is FeO2 deposits rather than scale so causing the problem on the CH side and not the HW?