Checking my earthing on SWA

Joined
9 Jan 2020
Messages
776
Reaction score
28
Country
United Kingdom
I've recently put some outside lights on some smallish SWA. I'm happy with how it has gone but not having done this before, I would like to double check my armour earthing on the gland fittings. Is there a normal way to do this? I was thinking along the lines of checking resistance somehow but it's a single run of cable 15m long so how would I?
 
Sponsored Links
The proper way, would be to use an Earth Loop Impedance tester. These check both that you have continuity and the value of the resistance/impedance.
 
If I have understood your question correctly:

I think you just need to measure the resistance between the armour itself and the earth connection to it - at both ends.

It should be all but zero Ohms.
 
If I have understood your question correctly:

I think you just need to measure the resistance between the armour itself and the earth connection to it - at both ends.

It should be all but zero Ohms.
I have 15m length with 3 boxes, so I think as you say I want to check that it's a good conductor from the last termination to the earth connection. But since the end is 15m from the supply, how can I physically do that as my multimeter obviously doesn't have 7.5m leads :)

I was thinking I could (temporarily!) connect the live to the earth terminal on the final box, then connect my multimeter to the live and earth connections at the the other end. I guess this tests the live at the same time - is this the sort of thing you meant?
 
Sponsored Links
I have 15m length with 3 boxes, so I think as you say I want to check that it's a good conductor from the last termination to the earth connection. But since the end is 15m from the supply, how can I physically do that as my multimeter obviously doesn't have 7.5m leads :)

I was thinking I could (temporarily!) connect the live to the earth terminal on the final box, then connect my multimeter to the live and earth connections at the the other end. I guess this tests the live at the same time - is this the sort of thing you meant?

You could do that, but only an impedance tester checks to the 'quality' of the terminations will stand up to a load. Put simply - You can measure a good low resistance with an ordinary meter, but under fault conditions and some current - the resistance of the connections can suddenly increase.
 
You could do that, but only an impedance tester checks to the 'quality' of the terminations will stand up to a load. Put simply - You can measure a good low resistance with an ordinary meter, but under fault conditions and some current - the resistance of the connections can suddenly increase.
That makes sense. I have my dad's kit but I'm not sure he had one of those - is it a specialist bit of kit? I can ask a pro to check it properly later, for now I just want to find obvious faults in case any of my mechanical gland fittings has an issue - I've given them all a good tug already.
 