Combi Boiler DHW Temperature Control

Joined
15 May 2022
Messages
2,955
Reaction score
722
Location
Cork
Country
Ireland
Most Combi Boilers now have DHW temperature control with setpoint temperatures down to 35C.
A 35 or 40kw bolier may only have a minimum output of say 6kw and and minimm DHW flowrate (DHW flowswitch trip) of 2.0LPM.
If a SP of 35C is selected then a flowrate of 3.44LPM will maintain that temperature of 35C (from mains at 10C). However if the flowrate is reduced to 2.5LPM then the DHW temperature will rise to almost 45C (44.4C), will the burner then cut out as the dT is 9.4C?. The boiler flow temperature on CH is allowed up to 5C > than its setting before burner trip. Does the same apply when on DHW?, ie burner cut out at DHW SP+5C?.
 
Sponsored Links

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top