Boiler is showing pressure at 0.0,
Tried filling from the loop but it does not change at all.
I cannot access the clock to check if the time is correct, because of this.
I have hot water and heating.
Any ideas as to what is the problem?
 
Last edited:
Sponsored Links
If you're sure you have pressure in the system then most likely a failed pressure sensor
 
  • Like
Reactions: CBW
Sponsored Links
It was doing exactly the same before the sensor was changed and changing it didn't resolve the issue
 
Are you sure you don't have a leak?

These boilers will run perfectly happily with the pressure sensor disconnected
 
No signs of a leak,
I might have a look tomorrow and disconnect the sensor
 
No signs of a leak,
I might have a look tomorrow and disconnect the sensor
Do not do that.
Disconnecting the sensor- is for open vented. You want to kill the boiler, go right ahead

Do you know for a fact boiler is not ejecting the system water? If the previous pressure switch was replaced because it was blocked with crud, no reason why same sediment could not be the case of system
Losing pressure
 
Last edited:
I can see any signs of ejected water.
The old pressure sensor wasn't blocked as far as i remember
 
I have heating and hot water.
I believe the system is full, bled the rads and no air escaped at all.
There is no fault light displaying as per the manual.
 
Last edited: