    I have a building which has and needs 3 phase power but I also have some machinery which I want to use that is single phase.

    So on a circuit that is currently 3 phase, what has to be done to turn it into single phase ?
     
  2. Sponsored Links
  3. conny

    conny

    Joined:
    30 Jun 2008
    Messages:
    12,610
    Thanks Received:
    550
    Location:
    Suffolk
    Country:
    United Kingdom
    You need a neutral and a qualified spark.

    In fact it's unusual not to have at least one single phase circuit.
     
  4. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    44,228
    Thanks Received:
    2,795
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    As has been said, you need an electrician - but, just to explain, one does not 'convert' 3-phase to single phase but, rather, one just ones one (or more) of the three phases (plus a neutral) as a single-phase supply. As has also been said, it's a very common situation, so any electrician should be familiar with it.

    Kind Regards, John
     
  5. wgt52

    wgt52

    Joined:
    25 Apr 2016
    Messages:
    702
    Thanks Received:
    130
    Country:
    United Kingdom
    Get an industrial electrician in to do the work. I presume the premises already have electrical socket outlets. It's possible to have different 'phases' in ajacent sockets which can be dangerous if not known about. A good electrician will know how to resolve it and warn about it.
     
  6. DetlefSchmitz

    DetlefSchmitz

    Joined:
    17 Aug 2010
    Messages:
    2,118
    Thanks Received:
    275
    Country:
    United Kingdom
    People often say this . I have often wondered why...
     
    • Like Like x 3
  7. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    44,228
    Thanks Received:
    2,795
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    Same here, in most senses - just like the excitement when two or more phases are present in the same enclosure - even though 230V PDs are plenty high enough to kill!

    In the current context, the one thing I would say is that if two 'adjacent' sockets are on different phases, they will inevitably be on different final circuits - so, as in any situation in which there were 'adjacent'/nearby sockets on different final circuits (whether the same or different phases), I'd perhaps be inclined to have some 'warning notices', pointing out that more than one circuit had to be isolated in order to kill all the sockets.

    Kind Regards, John
     
  8. DetlefSchmitz

    DetlefSchmitz

    Joined:
    17 Aug 2010
    Messages:
    2,118
    Thanks Received:
    275
    Country:
    United Kingdom
    Different circuits I sort of get. Though it is always said that if you don't check for dead then you are to blame for the consequences.

    Different phases just means that if you decided to connect something between live on two different sockets and expected the potential difference to be zero, you would get a surprise. Seems like a non-issue to me.
     
    • Like Like x 1
  9. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    44,228
    Thanks Received:
    2,795
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    Agreed - but whilst one obviously should not have to design on the basis of future stupidity, nearby sockets on different circuits are perhaps a 'tempting target' for such stupidity, and hence perhaps worth doing some 'warning' about.
    Quite so.

    I may be wrong (don't have my copy to hand), but I have a feeling that BS7671 dropped the requirement for a warning label about 'different phases in an enclosure', didn't it?

    Kind Regards, John
     
  10. Sponsored Links
  11. sparkwright

    sparkwright

    Joined:
    20 Aug 2009
    Messages:
    7,489
    Thanks Received:
    917
    Location:
    Dorset
    Country:
    United Kingdom
    I wouldn't mind Flameport doing one of his videos showing what happens when inserting something between two phases.

    With him kept safely away of course...
     
  12. sparkwright

    sparkwright

    Joined:
    20 Aug 2009
    Messages:
    7,489
    Thanks Received:
    917
    Location:
    Dorset
    Country:
    United Kingdom
    Assuming you have a 3 phase and neutral supply, and a 3 phase distribution board, single phase circuits can be created easily with single pole circuit breakers.

    This is work for electricians and not DIY work.
     
  13. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,784
    Thanks Received:
    2,857
    Location:
    London
    Country:
    United Kingdom
    There are DIYers here who would be quite capable of doing it.

    But the OP isn't one.
     
  14. sparkwright

    sparkwright

    Joined:
    20 Aug 2009
    Messages:
    7,489
    Thanks Received:
    917
    Location:
    Dorset
    Country:
    United Kingdom
  15. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    44,228
    Thanks Received:
    2,795
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    ... as 'entertainment', perhaps - but it's very hard to see how any such event is going to occur in practice (either accidentally or as the result of some deliberate action).

    A "video showing what happens when inserting something between L and N of one phase" might well be just as 'entertaining'!

    Kind Regards, John
     
  16. SUNRAY

    SUNRAY

    Joined:
    28 Jul 2009
    Messages:
    3,219
    Thanks Received:
    201
    Location:
    Kent
    Country:
    United Kingdom
    depending on the size of the OCD there may be very little difference.
     
  17. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    44,228
    Thanks Received:
    2,795
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    Exactly my point.

    As I've said, whether in terms of 'flashes and bangs' or the ability to kill, 230V pds are not necessarily going to be appreciably different from 400V - so, like Detlef, I'm not sure I really understand the excitement there often is about two phases being 'nearby' or 'in the same enclosure'.

    Kind Regards, John
     