    I managed to drill through a mains cable (idiot I know) over the weekend, which powered the booster in a storage heater. I repaired the wire using a connector block and covered the joint in insulation tape.

    First question is will this be a sufficient long term fix (it was a tight connection as there wasn't much slack in the wire) or is it worth replacing the whole cable? Second, is it ok to plaster over insulation tape?

    Thanks in advance for any help
     
  2. Sponsored Links
  3. davelx

    davelx

    Joined:
    26 Sep 2006
    Messages:
    1,625
    Thanks Received:
    126
    Location:
    London
    Country:
    United Kingdom
    Screwed connections must be readily accessible for inspection/tightening, so you cannot bury it in plaster.

    Best thing to do is to replace the cable.
     
  4. bernardgreen

    bernardgreen

    Joined:
    3 Nov 2006
    Messages:
    22,998
    Thanks Received:
    2,174
    Location:
    Bedfordshire
    Country:
    United Kingdom
    Replace the cable if you can.

    Plastering over a junction means it is no longer accessible hence it is against the regulations.

    The internal damage extends a long way inside of the cable and a weakened conductor could become a hot spot.

    This is one I did.

    The black is soot and copper particles.

    [​IMG]
     
  5. Chri5

    Chri5

    Joined:
    19 Jan 2007
    Messages:
    4,289
    Thanks Received:
    391
    Location:
    London
    Country:
    United Kingdom
    Crimp or solder, with sleeving / heat shrink to cover each of the conductors and the earth/ CPC.
     
  6. matt1234

    matt1234

    Joined:
    26 Mar 2007
    Messages:
    2
    Thanks Received:
    0
    Country:
    United Kingdom
    Thanks for replies. So the cable would have to be replaced right from the plug all the way to the source, where ever that is? That sounds expensive

    Think the soldering etc is beyond my capabilities. Would that be a cheaper possibility to get someone in to do that?
     
  7. davy_owen_88

    davy_owen_88

    Joined:
    17 Nov 2006
    Messages:
    1,680
    Thanks Received:
    2
    Location:
    West Glamorgan
    Country:
    United Kingdom
    ALL connections must be accessible unless they are made by soldering/brazing or by compression tool (crimps). It is best if all joints even those mentioned above are accessible because no joint is perfect but it isn't a requirement.

    Insulation tape is not a good enough covering because it dries out, the adhesive fails, it unravels and you are left with exposed joints.

    If it is possible then replace the whole cable, if not either leave the connector blocks accessible (cover with a blanking plate or a picture or something.) But if you must cover it over then crimping with heatshrink is the way to go.
     
  8. Sponsored Links
  9. emphasis303

    emphasis303

    Joined:
    31 May 2007
    Messages:
    369
    Thanks Received:
    0
    Country:
    United Kingdom
  10. peter2007

    peter2007

    Joined:
    14 Dec 2007
    Messages:
    1
    Thanks Received:
    0
    Country:
    United Kingdom
    I have just damaged a cable in my kitchen for my extractor hood putting in some new shelves :oops: . The cable was black and red. Can I replace the cable even though I would have to use new colours and is this notifyable as I am only replacing what is there? :cry: :?:
     
  11. plugwash

    plugwash

    Joined:
    28 Mar 2004
    Messages:
    9,086
    Thanks Received:
    297
    Country:
    United Kingdom
    IIRC replacing cable for an existing circuit is not notifiable even in a special location. Remember to stick the appropriate label next to the CU to warn people that both color codes are in use.
     
  12. Lectrician

    Lectrician

    Joined:
    18 Jul 2004
    Messages:
    8,399
    Thanks Received:
    380
    Location:
    Devon
    Country:
    United Kingdom
    But I am guessing that the cooker hood is in the kitchen.....
     
  13. plugwash

    plugwash

    Joined:
    28 Mar 2004
    Messages:
    9,086
    Thanks Received:
    297
    Country:
    United Kingdom
    looking at http://www.diynot.com/wiki/electrics:part_p:diy_electrical_work_and_the_law it looks lke according to the law replacing damaged cable for a single circuit only is not notifiable regardless of location.

    Part P is a bit confusing in this regard. Some stuff is notifiable whereever it is. Some stuff is notifiable in special locations, on special installations and in kitchens and some stuff is only notifiable in special locations.
     
  14. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Sponsored Links
Loading...

Share This Page