Hi,
Can anyone advise on how they would work out total demand including diversity in a situation with economy 7 storage heaters?
Working out the maximum demand on the main circuits gives me about 63A, which works out ok (the main house fuse is a 60A - the main CU has 100A isolation switch)
However, there are 3 storage heaters and a 3kw immersion heater on a separate economy 7 CU, all on 20A rewireable fuses.
The On site guide doesn't suggest what to do in this situation. Taking it directly would give maybe another 40A, but since these are only running overnight, when most of the other loads are off, is it reasonable to take the view that they can be ignored, or at least partially discounted?
Any thoughts on what is best practise in this situation would be appreciated.
Regards
Gavin
Can anyone advise on how they would work out total demand including diversity in a situation with economy 7 storage heaters?
Working out the maximum demand on the main circuits gives me about 63A, which works out ok (the main house fuse is a 60A - the main CU has 100A isolation switch)
However, there are 3 storage heaters and a 3kw immersion heater on a separate economy 7 CU, all on 20A rewireable fuses.
The On site guide doesn't suggest what to do in this situation. Taking it directly would give maybe another 40A, but since these are only running overnight, when most of the other loads are off, is it reasonable to take the view that they can be ignored, or at least partially discounted?
Any thoughts on what is best practise in this situation would be appreciated.
Regards
Gavin