E119 on Baxi Duo-Tec Combi HE 33 although pressurised

Joined
22 Mar 2010
Messages
2
Reaction score
0
Location
London
Country
United Kingdom
Hi all,

my almost new (installed in october) baxi combi HE 33 refuses to fire up although I have topped up the pressure to 1.5 as per the user manual.

The pressure had dropped zero as the the lads installing a new bathroom removed a bathroom heater

Any ideas to get this going again? Recharging the EXV, shorting the pressure switch sounds complicated + not sure where these are in the boiler :(

Thanks for your replies
Al
 
Sponsored Links
whats e119 again? low pressure? the pressure switches on these are ****e.
 
It would be very unusual for a pressure switch inlet pipe to be blocked by dirt after such a short time.

If not then it should be covered by the warrantee.

Tony
 
Not if it has been fitted to a dirty system......the amount of times i have seen 'flushed' systems that have been drained and refilled with fresh water a few times and called 'flushed'.......

The pressure switches on these are sensitive but not s~~te, ie they will show E119 at anything below 1 bar but it is usually the damn integral filling loop non return valve that sticks not the pressure switch.....just my observations of course
 
Sponsored Links
All sorted

The heater that was taken off broke the circulation of water in the system - hence the problem. Heater is back on, boiler is functioning

thanks for your replies
 
It sounds as if you had a single pipe system which is unusual!

But that would not have prevented the hot water working on a combi boiler.

Tony
 