Earth Leakage Tester, what should trip, MCB or RCCB? France

Discussion in 'Electrics Outside of the UK' started by dedee, 18 Mar 2011.

  1. dedee

    dedee

    Joined:
    23 Apr 2007
    Messages:
    9
    Thanks Received:
    0
    Country:
    United Kingdom
    I've just wired my workshop and bought an earth leakage tester to check the sockets were wired correctly, they were.

    When I tested the sockets they all trip the RCCB rather than the MCB at either 25 or 30mA. Is this normal?
    It is the same with the sockets that I have tested in the house.

    The consumer unit was installed by an electrician, all I have done is added 3mcbs ( Lights, sockets, and one for the heater). I've used 3 core, 2.5mm2 rigid cable for the sockets connected to a 20amp MCB (8 sockets). The consumer unit has a 40A 30mA RCCB.

    Many thanks

    Andy
     
  2. Sponsored Links
  3. solair

    solair

    Joined:
    22 Jan 2007
    Messages:
    93
    Thanks Received:
    8
    Country:
    United Kingdom
    MCBs are designed to protect a circuit against over-loading if too many devices are connected to it, or if there is a direct live to neutral short. This is what protects your house from burning down.

    The 20amp MCBs will trip if loaded beyond 20amps. They have a trip curve, which means that they will safely continue to operate for a little while if overloaded slightly before they trip where as with a serious overload / direct short they will trip fast. This is so that they can cope with motor start up surges etc.

    RCD (RCCB) is designed to prevent electric shock. They trip if the difference between live and neutral is more than 30mA (or, whatever the preset value is).

    Your earth leakage checker causing an earth leak i.e. it's connecting from the live to the earth and your RCB trips. This is perfectly safe and normal and what should happen.

    Your MCBs will only trip if the circuit's overloaded or there's a straight live-neutral short circuit.

    There's a small French distribution board:

    [​IMG]

    Btw : NEVER EVER EVER use 32A rings in France. They can only be used with fused plugs i.e. UK / Irish type plugs and sockets.
     
    • Thanks Thanks x 1
  4. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page