I wish to run a 10mm 2 core swa to the above approx 33m from house. Existing house ccu has no provision for RCD protection or spare ways so it's a tails split job.
Intention is to use armouring as cpc and bond it at house end only. My question is as there appears to be no extraneous conductive parts in the shed, does it require TT'ing?
Intention is to use armouring as cpc and bond it at house end only. My question is as there appears to be no extraneous conductive parts in the shed, does it require TT'ing?