I have a single socket above the counter which I believe to be a spur (single 2.5mm cable). The washing machine is plugged in to this. Can I run a 13a FCU from this socket, down to a single socket below the counter? Or is this spurring from a spur?
You already know the answer- it is spurring from a spur & not permitted. If you have the space, put an FCU (electrically) before your existing single socket- if you do that you can have as many 13A sockets as you like AFTER the FCU.
EDIT Or FCUs controlling other sockets or whatever
That is the traditional view, but I think you'd struggle to find a regulation which says that it was 'not permitted'. If the cable is 'clipped direct' 2.5mm² cable, there's nothing electrically wrong with it feeding one single socket plus one FCU, is there?You already know the answer- it is spurring from a spur & not permitted.
True, but since we know that one of the loads is a WM, there would at least be times when there was little/none of the 13A total 'left' for other sockets!If you have the space, put an FCU (electrically) before your existing single socket- if you do that you can have as many 13A sockets as you like AFTER the FCU.
Tee hee, nested quotes. Yerse, if it is all 2.5mm clipped direct, no insulation involved so the full 27A is available then yes a single socket and a single FCU wouldn't do any harm. Fun starts when the single socket gets replaced by a double.That is the traditional view, but I think you'd struggle to find a regulation which says that it was 'not permitted'. If the cable is 'clipped direct' 2.5mm² cable, there's nothing electrically wrong with it feeding one single socket plus one FCU, is there?You already know the answer- it is spurring from a spur & not permitted.
True, but since we know that one of the loads is a WM, there would at least be times when there was little/none of the 13A total 'left' for other sockets!If you have the space, put an FCU (electrically) before your existing single socket- if you do that you can have as many 13A sockets as you like AFTER the FCU.
Kind Regards, John
As I implied, unless you can find a regulation which 'disallows it', and provided the cable is clipped direct, then it could easily be argued that to 'spur an FCU off a single spurred socket' (thereby increasing total available current from 13A to 26A) would be compliant with the regs!This is true, but I suppose it depends how often the machine is in use! So long as the other socket isn't going to be for a tumble dryer, I wouldn't be overly concerned. Perhaps not the best solution but is there another way around it?
If this is in a kitchen and someone might want to plug a kettle into that socket, then you have a risk of blowing the fuse in the FCU.
This sort of arangement is more useful when the attached loads are likely to be small, e.g. a row of sockets behind a TV etc.
This is true, but I suppose it depends how often the machine is in use! So long as the other socket isn't going to be for a tumble dryer, I wouldn't be overly concerned.
Perhaps not the best solution but is there another way around it?
That is the traditional view, but I think you'd struggle to find a regulation which says that it was 'not permitted'. If the cable is 'clipped direct' 2.5mm² cable, there's nothing electrically wrong with it feeding one single socket plus one FCU, is there?You already know the answer- it is spurring from a spur & not permitted.
True, but since we know that one of the loads is a WM, there would at least be times when there was little/none of the 13A total 'left' for other sockets!If you have the space, put an FCU (electrically) before your existing single socket- if you do that you can have as many 13A sockets as you like AFTER the FCU.
Kind Regards, John
Indeed - and not only wouldn'd it do any harm but, as far as I can see, it would be regs-compliant.Yerse, if it is all 2.5mm clipped direct, no insulation involved so the full 27A is available then yes a single socket and a single FCU wouldn't do any harm.
Yes, but one cannot really make provision for what unacceptable changes may subsequently be made to the installation -f we took that approach, we couldn't do anything!Fun starts when the single socket gets replaced by a double.
Yes, but how do you make sure that everyone who may use the room knows, and always remembers, all that?!Re the available capacity- true but as long as you don't fully load both sockets at the same time it'll be fine. So don't boil the kettle while the washer is running, definitely don't run the tumble dryer from that socket while the washer is running
Not buried in insulation or suchlike. Either on the surface or buried in plaster counts as 'clipped direct', in which case 2.5mm² cable can carry up to 27A.Can you explain what you mean by clipped direct?