Feed and expansion tank

Joined
21 Sep 2009
Messages
7
Reaction score
0
Location
Lancashire
Country
United Kingdom
Can anyone tell me what the correct distance is for the open vent termination to the water level in the F&E tank ????

Thanks

:(
 
Sponsored Links
No there is a set recommended max distance in the regs.
I got shot the question in a job interview believe it or not and its really got me going to find the distance - it's defo in mm and its something like 50mm - 100mm etc.
 
Sponsored Links
"Vent pipe shall terminate not less than twice the internal Diameter of the vent pipe above the top of the float operated valve or top of the overflow pipewhichever is the higher"

Edit: the pic shows the top of the float valve being the very top of the white plastic water spout. The top of the Overflow being the top of the overflow pipe (obviously)
 
Or as Kev said just above the overflow outlet, how far don't make an monkeys difference provided it's below the rim of the tank.
 
Thanks to all who replied especially bathstyle!!!
If I dont get the bloddy job now I never will!!!

Thank you all !

:D :D :D
 