Ferroli Modina 102

Joined
2 Mar 2007
Messages
2
Reaction score
0
Location
Gwent
Country
United Kingdom
Im after any helpful advice. The last few weeks my DHW has been cold and i have had to turn it of and back on a few times then its ok. the CH is functioning correctly. The tap symbol light is not on when the fault occurs but the CH stand by led is flashing. the manual says to look at the flow meter can any one confirm this. also do they just stick and need cleaning up or do they need changing. Stocky
 
the flow switches are prone to fail on this and they dont clean up too well.....better to replace. nice easy job.
 
Thanks. what about the filter and limiter do they clog up in general i will probably check these and if all ok will replace flowmeter.
 
If they havn`t been changed in a few years I`d change both thermistors as well,while youve got the case off.
JonB
 