Fire protection for RSJ / UB - Quick Question.

Discussion in 'Building' started by MonkeyHunter, 11 Nov 2008.

  1. MonkeyHunter

    Joined:
    5 Jul 2007
    Messages:
    101
    Thanks Received:
    0
    Location:
    Bristol
    Country:
    United Kingdom
    Hi,

    If a RSJ is fully enclosed in a wall, does it need additional fire protection, or is 12.5mm Plasterboard + skim sufficient, as when a beam is enclosed within a ceiling?

    cheers!
     
  2. Shytalkz

    Joined:
    22 Feb 2008
    Messages:
    4,864
    Thanks Received:
    14
    Location:
    Norfolk
    Country:
    United Kingdom
    If you mean it's brick/blocked around, then yes that's fine without anything else.
     
  3. MonkeyHunter

    Joined:
    5 Jul 2007
    Messages:
    101
    Thanks Received:
    0
    Location:
    Bristol
    Country:
    United Kingdom
    Thanks for the reply, sorry should have said it's a stud wall that encompasses the rsj.
     
  4. Shytalkz

    Joined:
    22 Feb 2008
    Messages:
    4,864
    Thanks Received:
    14
    Location:
    Norfolk
    Country:
    United Kingdom
    You're still ok with that.
     
  5. MonkeyHunter

    Joined:
    5 Jul 2007
    Messages:
    101
    Thanks Received:
    0
    Location:
    Bristol
    Country:
    United Kingdom
    That's great, thanks for your reply's Shytalkz.
     