Fuse and cable for a cooker
10 Aug 2005
Hi
Am new to electrics and have a couple of quick questions.
I have a new electric cooker rated to a max of 10.8kw and a cooker isolation switch with an integral socket.
What fuse do i need in the fuse box (Is the 30A fuse that is already there enough?)
And, what cable size and type should I use to connect between the cooker and the connection plate (6 mm or 10 mm and i assume it is two core and earth type)
Any help would be much appreciated.
Thanks in advance.
10.8kW divided by Voltage = 46.95Amps
You will need a 50Amp fuse and 10mm cable from fuse box to Cooker control point.
Never connect a larger cable to a smaller feed cable.
ive just spurred off a dbl socket with 2.5 t/e to a 3 amp fused spur then a piece of 1.5 from there to gas fire for ignitor so are you saying dont do that cus im going from larger cable to smaller :?: cheers P M
2.5 spurs off rings are perfecly ok, and the 1.5 is ok because its fused down first
Poshman
I said don't connect larger cables to smaller feed cables.
i.e. 4mm to a 2.5mm radial
Diversity?
Diversity?
Now I'm confused, will diversity affect my requirements much?
So based on diversity (and your above calculation) a 30A fuse will be ok for the 10.8kW cooker. (Want to get this right - don't want to blow the fuse as soon as i turn the cooker on). :D :shock: :D
oops, the diversity calc was wrong. Need to allow 5A for the socket. So you need the next size MCB up from that.