• Looking for a smarter way to manage your heating this winter? We’ve been testing the new Aqara Radiator Thermostat W600 to see how quiet, accurate and easy it is to use around the home. Click here read our review.

Fuse and cable for a cooker

Joined
10 Aug 2005
Messages
4
Reaction score
0
Country
United Kingdom
Hi

Am new to electrics and have a couple of quick questions.

I have a new electric cooker rated to a max of 10.8kw and a cooker isolation switch with an integral socket.

What fuse do i need in the fuse box (Is the 30A fuse that is already there enough?)

And, what cable size and type should I use to connect between the cooker and the connection plate (6 mm or 10 mm and i assume it is two core and earth type)

Any help would be much appreciated.

Thanks in advance.
 
10.8kW divided by Voltage = 46.95Amps

You will need a 50Amp fuse and 10mm cable from fuse box to Cooker control point.

Never connect a larger cable to a smaller feed cable.
 
ive just spurred off a dbl socket with 2.5 t/e to a 3 amp fused spur then a piece of 1.5 from there to gas fire for ignitor so are you saying dont do that cus im going from larger cable to smaller :?: cheers P M
 
2.5 spurs off rings are perfecly ok, and the 1.5 is ok because its fused down first
 
Poshman
I said don't connect larger cables to smaller feed cables.
i.e. 4mm to a 2.5mm radial
 
Qedelec said:
10.8kW divided by Voltage = 46.95Amps

You will need a 50Amp fuse and 10mm cable from fuse box to Cooker control point.

Never connect a larger cable to a smaller feed cable.

Diversity?
 
slippyr4 said:
Qedelec said:
10.8kW divided by Voltage = 46.95Amps

You will need a 50Amp fuse and 10mm cable from fuse box to Cooker control point.

Never connect a larger cable to a smaller feed cable.

Diversity?

Now I'm confused, will diversity affect my requirements much?
 
So based on diversity (and your above calculation) a 30A fuse will be ok for the 10.8kW cooker. (Want to get this right - don't want to blow the fuse as soon as i turn the cooker on). :D :shock: :D
 
oops, the diversity calc was wrong. Need to allow 5A for the socket. So you need the next size MCB up from that.
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top