Glow worm 40ff Boiler

Joined
26 Feb 2010
Messages
1
Reaction score
0
Location
Nottingham
Country
United Kingdom
HI,

I recently moved house and wanted to get a new kitchen. So I moved the boiler so it can fit in one of the units. Thats where the problem started. After the completion of relocation the boilr didn't run. The fan was running but the air doesn't come through the pipe. The installer removed the pipe and blew air from mouth. It ran succesfully but as soon as he stopped blowing boiler turned off. I was told to get I new PCB which I did but still the same problem.

I already spent £300 on this boiler. Can anyone help me in this? What is the problem with the fan? why it is not sending the air?

I am really upset about this.
 
with the weekend coming up, ask the installer to keep blowing until monday, then it can be his first job to fix it
 
Old boilers don't always like being moved.

Job for a RGI. Would suggest the fan venturi is blocked or the tubes are. If the last bloke blew right into the tube he may've damaged the air pressure switch too.
 