• Looking for a smarter way to manage your heating this winter? We’ve been testing the new Aqara Radiator Thermostat W600 to see how quiet, accurate and easy it is to use around the home. Click here read our review.

Glow-worm override problem...

Joined
18 Apr 2010
Messages
53
Reaction score
2
Location
London
Country
United Kingdom
Hello guys... i've got a glow worm boiler Flexicom 30 cx.
It works fine as I programmed it.

I set the system to keep the house heat not to go below 18 for the afternoon period. But sometimes it feels cold so I need to override the system.

I have the wireless controller Climapro RF, I do the override by pressing the up arrow button. it asks for what temp i want and till when.

I set them and see the display shows a note of override but the boiler doesn't respond and doesn't fire up.

I even took the controller and put it near the boiler but it didn't work.

Any ideas?
 
if its a climapro 2 then you need to change the date back to anything other than 2012 and it will work as normal, it has a software issue that appeared when the year turned. let glowworm know and they will come and change it when they find a fix.
 
if its a climapro 2 then you need to change the date back to anything other than 2012 and it will work as normal, it has a software issue that appeared when the year turned. let glowworm know and they will come and change it when they find a fix.

Thanks a lot mate... I took the date back to 2011 and it worked...

many thanks :)
 
This has been bugging me for weeks, kept thinking that the Climapro 2 was on its way out! Changed it back to 2011 and its fine.

Its like the millennium bug all over again. Thanks a lot! :D
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top