Glow Worm SpaceSaver 50BF Boiler

Joined
22 Dec 2010
Messages
2
Reaction score
0
Location
Manchester
Country
United Kingdom
Can anyone help.
My boiler has been working for years with no problems. Suddenly it is producing soot at a rapid rate despite cleaning. A plumber has been today and suggested the Burner, aeromatic 7/51995 unit is at fault as everything looks OK.
However this part is not available thus my faithful boiler will be condemmed.
Does anyone know where I may obtain this part or is it possible to get it cleaned/refurbished.
Desperate as I now have no heat or more urgent-- Hot Water
 
Unless the burner is damaged there is no way that it should need replacement.You need to get a proper boiler engineer to overhaul your boiler correctly.Sooting is a servicing issue that should be easily done especially on such a simple boiler.
 
Having to ask whether burner can be cleaned surely the guy you have looking at it would know that.
Basically you stick it under the tap and wash it out
 
Has he checked seals and flue. has he cleaned heat exchangerTHOROUGHLY. Gas rate tested? It is fairly unusual for these to soot up
 
Thanks Guys. The boilerman has taken away this part for cleaning and has not returned it yet despite phones call. Promised 29 and 30th December but nothing and now I have a serious chest infection.

Thought it strange that the burner could be the root of the soot problem.
 