The carp filling loop will be coming off just as soon as they have gone, I asked them for 2 sealing washered caps to put there instead. The ugly bit can go in a cupboard.
You're missing the point. The double check valve is supposed to go on the mains side to prevent back flow in compliance with Reg. 24.
Fitted on the heating side the double check valve often fails meaning when you disconnect the loop you have water at system pressure leaking back through the check valves, hence the majority of these loops remain connected in contravention of the regs and increasing the risk that the system pressure rises due to the filling valve letting by slightly (they are often very poor quality).
Proper loops have valves at each end of the loop (so you turn both off, remove the link and fit the protective end caps).
I suggest you ask them how they intend the installation to comply with the water regulations.
It pi**es me off thet merchants are permitted to sell this carp and installers then fit it to save a couple of quid.
Compare the figures in the benchmark with the figures quoted in the manufacturers instructions...really dumb installers copy the data exactly so it's very obvious they haven't done the calculations necessary. eg the gas rate.