Greenstar 30si, cold radiators

Joined
6 Jan 2012
Messages
6
Reaction score
0
Location
Lancashire
Country
United Kingdom
Have hot water at the taps, but as in the title cold radiators.
The pressure is reading 1.5, the controll for the system has new batteries in. The system is 4 years old and has been serviced reguarly, the chap we use is currently on holiday, hence my post. Hope someone can help, thanks in advance.
 
Vague I know, sorry. Not my strong point knowing my way round anything like this.
There is no sign of the boiler kicking in what so ever for the central heating.
 
Can you confirm if the boiler is responding to the call for heat? Dies it get warm, but not send the heat to the rads, or does it just sit there looking pretty?

If you can't answer these questions then you need to think about getting an RGI or Worcester out to the boiler.
 
No I haven't, I was hoping that it may have been something simple that I'd overlooked, but after searching the Worcester website and many other forums for anyone with the same problem and coming up blank. I think It's time to call a alternative engineer.
 
That's why I'd rather not play around with something that I could potentialy cause more problems.
Thank you for the replies, Andy.
 
Problem solved, after speaking to a engineer they suggesed that after replaicing the batteries the boiler may not be picking up the signal.
To resolve this, removed batteries put the timer infront of boiler re-inserted batteries put timer into a activated possition, and boiler kicked in. Timer now put back in its regular possition.
Was told this is a common thing that happens, hope it may help someone else.
 