It says you must have zones, but nothing about how the zones are formed, TRV according to a number of council websites are considered as forming zones.
It says you must have zones, but nothing about how the zones are formed, TRV according to a number of council websites are considered as forming zones.
I replaced just the microswitch. I plugged the L/N of the motor into a test block and the motor was working fine turned into fully open position, which further pointed to the switch. After opening, pressing and depressing the switch wasn't completing the circuit.
Hi all - sorry to resurrect such an old thread but I have exactly the same issue as the original post. Basically it’s a 2 zone system with upstairs separate to downstairs and 2 thermostats (one upstairs and one downstairs). When i turn the downstairs thermostat on it clicks and opens the motorised valve but then no demand is requested from the boiler and the heating doesn’t come on. When I then go upstairs and turn the upstairs thermostat on the upstairs rads come on as usual but now the downstairs also works. So far I have replaced the downstairs thermostat (existing was Honeywell DT1) with a Honeywell DT2 and I have replaced the full motorised head with a replacement 2 port Honeywell head but the problem still persists. Any ideas really appreciated as I was thinking of replacing the upstairs head as well but I am not really sure why
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local