It's amazing how the so-called experts on here can't work out circulation pump head or duty................ 
If he wants to run everything at once a 25/80 may well be the solution, but he still needs to balance the whole lot...
It's amazing how the so-called experts on here can't work out circulation pump head or duty................![]()
It's amazing how the so-called experts on here can't work out circulation pump head or duty................![]()
Others here hide their true identity and make their profiles hidden!
Tony
how come GW, I was always taught 15/50 up to 24kws, and a 15/60 for 30 kws.
It's amazing how the so-called experts on here can't work out circulation pump head or duty................![]()

It's amazing how the so-called experts on here can't work out circulation pump head or duty................![]()
Others here hide their true identity and make their profiles hidden!
Tony
.
Any sealed Central Heating system works like the Big Wheel in the Fair Ground, if the circulation pump can lift water to the top of the wheel, gravity helps bring it back down again.
remembering things like a 15mm pipe can carry up to 4.9KW on a 11°C Delta T
.
Any sealed Central Heating system works like the Big Wheel in the Fair Ground, if the circulation pump can lift water to the top of the wheel, gravity helps bring it back down again.
Really! , me not think so., total resistance needs to be taken into acount and not just to the top of the wheel.
![]()
remembering things like a 15mm pipe can carry up to 4.9KW on a 11°C Delta T
Nope. .145 x 11 x 4.2 = 6.7 kw., you gotta know your onions delta.
![]()
.
Any sealed Central Heating system works like the Big Wheel in the Fair Ground, if the circulation pump can lift water to the top of the wheel, gravity helps bring it back down again.
Really! , me not think so., total resistance needs to be taken into acount and not just to the top of the wheel.
![]()
remembering things like a 15mm pipe can carry up to 4.9KW on a 11°C Delta T
Nope. .145 x 11 x 4.2 = 6.7 kw., you gotta know your onions delta.
![]()
Sorry mate that was for Pex, you're correct for copper tube.